I have a question about electrical service (I admit I really don't know a lot about this stuff).

In my panel I have a dedicated circuit for my bandsaw. It has 2 20A breakers ganged together and wired to a single 220 outlet. Is this a 20A circuit or a 40A circuit?

I am trying to figure out if I can plug my 28A table saw into this outlet.


_________________
Brock Poling
Columbus, Ohio
http://www.polingguitars.com


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 8:15 am 
Offline
Brazilian Rosewood
Brazilian Rosewood

Joined: Sat Dec 03, 2005 10:04 am
Posts: 2060
20A.

Twice the wattage of a 20A 110V circuit by means of doubling the Voltage,
but the amperage rating stays the same.

What on earth motor do have that's rated at 28A? That would be enough
amperage to power a 7 or 8 hp motor at 240v.

Are you sure the 28A rating is for 220, or is that the 110 rating (which
would put the 220 at 14A)?

_________________
Eschew obfuscation, espouse elucidation.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 8:57 am 
Offline
Old Growth Brazilian Rosewood
Old Growth Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 1:20 pm
Posts: 5915
Location: United States

It is a Grizzly 1023ZX 5HP 220V 10" Cabinet saw.

The manual says it needs to draw 28A.


_________________
Brock Poling
Columbus, Ohio
http://www.polingguitars.com


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 8:58 am 
Offline
Cocobolo
Cocobolo

Joined: Sun Mar 11, 2007 4:09 am
Posts: 252
Location: United States
Actually according to the NEC, the full load current of a 230V 5hp 1ph motor is 28A. Of course, you need to look at the nameplate to get the actual rating, but the NEC is usually pretty darned close to nameplate.  Double check the nameplate and make sure you aren't reading the wrong amperage rating if you have a smaller motor.  Many motors are dual voltage and have ratings that look something like this  Voltage 115/230  Amperage 16/8.8 .  The first voltage goes with the first amperage, the second goes with the second.  If it really is 28 amps nameplate, code requires the circuit be 125% of the nameplate which would be 35 amps.  That is #8 copper on a 40 amp breaker (40 amp double pole both breakers rated at 40 amps.)  You could go with a 35 amp breaker, but good luck finding one!





Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 8:59 am 
Offline
Cocobolo
Cocobolo

Joined: Sun Mar 11, 2007 4:09 am
Posts: 252
Location: United States
Whoops, Brock you were posting as I was writing!


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 9:10 am 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Wed Feb 01, 2006 3:25 am
Posts: 3788
Location: Russellville, Arkansas


Check the Motor for a plate similar to this one.

It gives two voltages, then two amperages, normally.

Evidently this motor will run on 208, so it has a third voltage and amperage.

This motor will run on the following: 115 Volts at 17.4 Amps, or 208 Volts at 8.9 Amps, or lastly at 230 Volts at 8.7 Amps. Your choice of breakers is 30 amp single pole 115 Volts, or double pole 20 amps 23 Volts.

The reason you need a 30 instead of a 20 on the 115 Volt circuit is the 80 percent rule of use on a breaker. A 20 amp will only net you output of 16 amps, so you have to go 30 amps which nets you 24 amps, if you run a 115 V. Circuit.

This is the math, not for your motor, which we are unsure of, but the label above for a motor on Ebay. Ebay is a great place to get electric motors for a fraction of it's value.

Good luck, get it right. Know the definition of Ampacity.

_________________
http://www.dickeyguitars.com


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 11:33 am 
Offline
Koa
Koa

Joined: Thu Nov 10, 2005 12:43 pm
Posts: 1031
Location: United States
Looks like we have a good supply of very competent electricians. All correct info.

Al


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 12:36 pm 
Offline
Koa
Koa
User avatar

Joined: Sat Jul 01, 2006 5:55 am
Posts: 1392
Location: United States
First name: James
Last Name: Bolan
City: Nashville
State: Tennessee
Country: USA
Plug it in and see if it throws the breaker.If not, your in there.
                  James

_________________
James W Bolan
Nashville Tennessee


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 1:18 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood

Joined: Sat Dec 03, 2005 10:04 am
Posts: 2060
And just to make sure you know, you certainly should never just replace a
breaker with a larger one.

If it has a 20 amp breaker right now, that probably means it has 12 gauge
wire running to the outlet. If you were going to up the breaker to 40
amps there are a few other things to consider. Of course the overall
rating and load of the box as a whole, and you would need 8 awg wire
past the breaker to meet standard electrical codes. Even that can depend
on the length of the run, and things like a 90 degree turn may equal 10
or 20 feet, and it may even differ depending on whether you are running
in conduit, rafters, or in a wall.

Check with your local codes (or better yet, a local electrician) to make
sure. But don't just change to a larger breaker because it's popping.

_________________
Eschew obfuscation, espouse elucidation.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 1:32 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood

Joined: Sat Dec 03, 2005 10:04 am
Posts: 2060
I should say that I bring this up because my brother just had a house fire
start inside a wall a few weeks ago due to a stupid mistake someone made
20-some years ago, before he bought the house. The fire department was
there in about 10 minutes, and all that was damaged was one interior wall,
the electrical, and smoke damage to a few rooms. It could have been much
worse.

Wiring is certainly not something suitable for jury-rigging. Make it right.

After all, it is National Fire Prevention Week, ya know.

_________________
Eschew obfuscation, espouse elucidation.


Top
 Profile  
 
 Post subject:
PostPosted: Mon Oct 08, 2007 10:36 pm 
Offline
Brazilian Rosewood
Brazilian Rosewood
User avatar

Joined: Wed Feb 01, 2006 3:25 am
Posts: 3788
Location: Russellville, Arkansas
Something tells me Brock is going to be running new service from the panel. But oh what a joy running a great cabinet saw can be.... oh yeah!

_________________
http://www.dickeyguitars.com


Top
 Profile  
 
 Post subject:
PostPosted: Tue Oct 09, 2007 12:45 am 
Offline
Mahogany
Mahogany

Joined: Sat Oct 06, 2007 10:08 am
Posts: 40
Location: United States
The manual downloaded from the Grizzly site says "The motor supplied
with the Model ZX is a 5HP 220V single-phase motor.  Under normal
use, the motor draws approximately 25 amps.  Use a 30-amp circuit
breaker or 30amp slow blow fuse for 220V operation."



Then they describe the NEMA L6-30 plug and socket they recommend for wall termination, and recommend a dedicated circuit.



If they have upped this recommendation since this manual was created,
then you should go for the 40amp circuit and an upgraded plug/socket.


_________________
-donh-

Everything is a tone control!


Top
 Profile  
 
 Post subject:
PostPosted: Tue Oct 09, 2007 1:16 am 
Offline
Old Growth Brazilian Rosewood
Old Growth Brazilian Rosewood
User avatar

Joined: Mon Dec 27, 2004 1:20 pm
Posts: 5915
Location: United States
[QUOTE=Bruce Dickey] Something tells me Brock is going to be running new service from the panel. But oh what a joy running a great cabinet saw can be.... oh yeah![/QUOTE]

Yes, this will be a new circuit. I actually had an electrician come out and install a new sub panel for me (I think it is a 100A service -- it's half as big as the main panel)

It only has 2 circuits in it now, the one for the bandsaw, and another for a 20A receptical.

I feel comfortable wiring recepticals etc (provided I know what the right ratings are on parts etc.) but I don't feel comfortable doing panel work.

Afterall... this is in my house where my kids sleep.   

_________________
Brock Poling
Columbus, Ohio
http://www.polingguitars.com


Top
 Profile  
 
 Post subject:
PostPosted: Tue Oct 09, 2007 1:22 am 
Offline
Koa
Koa

Joined: Wed Jun 01, 2005 6:35 am
Posts: 1325
Location: Kings Mtn., NC, USA
First name: Bill
Last Name: Greene
City: Kings Mountain
State: North Carolina
Zip/Postal Code: 28086
Country: USA
Focus: Build
Status: Amateur
I had the pleasure of meeting, and hanging out with, Al Peebels for a few hours on Saturday. Among other things, Al works tests and rebuilds large electric switch controllers for nuclear power plants.

He was testing circuits on some of their "smaller" machinery with 6000+ amps - on a machine that runs to 100,000 amps. Scary, scary stuff.

Bill, who can't rewire a light switch

_________________
Eagles may soar, but weasels don't get sucked into jet engines.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 14 posts ] 

All times are UTC - 5 hours


Who is online

Users browsing this forum: No registered users and 16 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
Powered by phpBB® Forum Software © phpBB Group
phpBB customization services by 2by2host.com